When grounding a tall tower in a rocky island, can we just throw a couple naked cables in the sea? If not, why not?
Please provide real-world examples if known.
When grounding a tall tower in a rocky island, can we just throw a couple naked cables in the sea? If not, why not?
Please provide real-world examples if known.
In principle, yes - all you need is a sufficiently good connection to ground, and saltwater will certainly provide that. Single Wire Earth Return power transmission systems can use this for return power; they usually use titanium grid electrodes to prevent corrosion.
Rocky soil does not offer a good resistivity, so that typical methods of driving electrodes into the soil will not reach a satisfactorily low earthing resistance.
It is assumed that the supply earthing is coming from the distribution network (at some extent utility), the purpose of local earthing is protection against lightning. It is a tall tower, on an island, so the risk assessment will come up with a large equivalent capture area, and correspondingly the need for an efficient Lightning Protection System. Required earthing resistance is 10 ohm or less (IEC 62305). If expecting very large lightning current (near or above cat. I of 62305; e.g. it happened in Malaysia ... >300 kA recorded!), resistance shall be correspondingly reduced.
Earthing with electrodes in the sea is possible and acceptable, provided that: