I am setting up my home security system. It calls for a 5.6 ohm resistor at the end of the line with smoke detectors. Does it matter what wattage? Can I get by with 1/4 watt?

JRE
  • 71,321
  • 10
  • 107
  • 188
C.W.
  • 29
  • 1

1 Answers1

8

I suspect it's supposed to be 5.6kΩ, because that's a standard.

EOL resistor in fire alarm systems

1/4W should be okay since voltage will be 12V or so (P=E²/R, thus 144V²/5600Ohm ~ 26mW).

As user253751 mentioned: the reason that end-of-line resistors are used is so that the alarm can sense whether the wire is broken. If the wire is broken the resistance will change (usually to zero or infinity)