1

I'm trying to follow an example of this, but I get a wildly different answer than expected and I can't see where I'm going wrong.

The example I've got, is for a 2.8 m steel column (RHS 150 x 100 x 5mm) fixed both ends with a simple static vertical central load. Couldn't be easier for a beginner. My calculation is:

Relevant properties (section properties taken from [here][1]) normalising length to metres:

  • Steel section: RHS 150 x 100 x 5mm. (unspecified hot or cold)
  • L: Free length = 2.8 m
  • E: 205 x 109 = 2.05 x 1011
  • I (table): Least 2nd moment of area = 3.923 x 106 mm4 = 3.923 x 10-6 m4
  • A (table): Area = 2373 mm2 = 2.373 x 10-3 m2
  • r (table): Least radius of gyration (as double check): 40.7mm = 0.0407 m
  • K: Effective length factor = 1 (fixed-fixed)
  • s: Slenderness = L/r = 2.8/0.0407 = 68.8 (intermediate)

EUler buckling force, calculated using I,K,L:

  • π2 x (E.I) / (KL)2
    = (3.1422 x (2.05 x 1011) x (3.923 x 10-6) / (1 x 2.8)2
    = 1.012 MN

Euler buckling force, calculated using A,s (as double check):

  • π2 x (E.A) / (s2)
    = π2 x (2.05 x 1011) x (2.373 x 10-3) / (68.8)2
    = 1.014 MN

So the two calculations agree within the limits of the data table figures.

The problem is, the correct answer is apparently Pc (compressive strength) = 124 N/mm2 = 294 kN.

The answer does confirm that slenderness is 68.8, and that the least radius of gyration is 40.7 mm, so I know I'm on the right track.

But there's no actual full calculation, and the error isn't an obvious factor that might suggest the problem, so I don't actually understand where Ive gone wrong.

(The actual question is part of a longer worked example, so if I get stuck anywhere else I might need to update this. But for now, that's the point I'm stuck at... )

Stilez
  • 571
  • 8
  • 19

1 Answers1

1

You've calculated the Euler buckling force, not the compressive strength. The part of the code you want is EN 1993-1-1 section 6.3.1, which specifies how to account for imperfections and safety factor in order to calculate the allowable load. The size of the imperfections depend on whether the profile is cold formed or hot finished and the relevant safety factor is defined in whatever national annex is applicable to your column.

ingenørd
  • 1,288
  • 7
  • 13